Ah, That's what was missing.
I was waiting for some more information as to what your issue was and didn't tie the two posts together.
Ok So your showing a battery bad and a raid controller issue.
Lets look at the CIM output and in the data we look for 2 data points that need to be with in the same element.
- "Element Name =" - Name of hardware item
- "Element Op Status =" - status of hardware item (0 and 2 are considered healthy in all systems but HP also uses 5)
Most hardware follows a common default CIM status code set. HP on the other hand did not. HP used the status of 5 as a "Good" code as well among other differences.
You show a HP ProLiant
- Screenshot 2022-10-03 084409.png (15.01 KiB) Viewed 6261460 times
Taking the first of the two error reports you show in your example.
The Battery Bad Issue
The CIM Data returned for that is
20220927 17:23:21 Element Name = Battery 1 42-SuperCAP Max
20220927 17:23:21 sensorType = 2 - Temperature
20220927 17:23:21 BaseUnits = 2
20220927 17:23:21 Scaled by = 0.010000
20220927 17:23:21 Current Reading = 29.000000
20220927 17:23:21 Upper Threshold Critical = 65.000000
20220927 17:23:21 Element Op Status = 2
The element
Battery 1 42-SuperCAP Max shows a status of 2 which as for the HP types list is an "OK". Now this is a status of the time of the scan and as such the status of the element may had changed. ESX maybe keeping a cache of or history I'm not aware of. I can't say so you would need to know your hardware and maybe preform some system tests to confirm failures.
As for the
HP Smart Array, the logs do not show a status for that element.
20220927 17:23:20 Element Name = Add-in Card 11:3
20220927 17:23:20 Element Op Status = 0
20220927 17:23:20 Element Name = Hardware Management Controller (Node 0)
20220927 17:23:20 Element Name = HP Smart Array P420i Controller : Embedded : HPSA1
20220927 17:23:20 Check classe CIM_NumericSensor
20220927 17:23:21 Element Name = System Board 10 Power Meter
20220927 17:23:21 sensorType = 4 - Current
20220927 17:23:21 BaseUnits = 7
20220927 17:23:21 Current Reading = 90.000000
Element Name = HP Smart Array P420i Controller : Embedded : HPSA1 is followed by another Element Name but returns no Element status.